My first thought is that this might be an issue with "net", or "total", or "incident" heat flux. Depending on the device, sometimes we measure a "gauge" heat flux. As I recall, some of the devices used in these experiments measured the heat flux to the hot wall, as opposed to a cold water-cooled heat flux gauge. Take a look at all output columns with heat flux and see if any match with what is in the guide. |
Beta Was this translation helpful? Give feedback.
0 replies
-
|
Kevin,
Thanks for the quick response. I noted the aspect you mention here as it appears in Section 10.1 (pg 127) of the V&V Guide. However, wouldn't that only affect the model output v the empirical test results? I'm looking at running v7.7.5 for NIST/NRC_T8.in and getting the same results that are presented, in chart form, for the same input file and the same version of CFAST, v7.7.5. Unless you altered the *.csv files, my output of v7.7.5 should be identical to yours, as long as I'm reading the right columns. I couldn't find any other columns or any other *.csv that gave flux results to match those curves in the V&V Guide, even when in validation output mode.
Thanks
Ray
From: Kevin McGrattan ***@***.***>
Sent: Thursday, February 5, 2026 4:45 PM
To: firemodels/cfast ***@***.***>
Cc: sprankleray ***@***.***>; Author ***@***.***>
Subject: Re: [firemodels/cfast] Surface Wall Flux Validation (Discussion #2230)
My first thought is that this might be an issue with "net", or "total", or "incident" heat flux. Depending on the device, sometimes we measure a "gauge" heat flux. As I recall, some of the devices used in these experiments measured the heat flux to the hot wall, as opposed to a cold water-cooled heat flux gauge. Take a look at all output columns with heat flux and see if any match with what is in the guide.
-
Reply to this email directly, view it on GitHub<#2230 (comment)>, or unsubscribe<https://github.com/notifications/unsubscribe-auth/AFZGHI5RN5URQOFI7EG6YA34KO2WPAVCNFSM6AAAAACUEWIPUCVHI2DSMVQWIX3LMV43URDJONRXK43TNFXW4Q3PNVWWK3TUHMYTKNZRGIYDENY>.
You are receiving this because you authored the thread.Message ID: ***@***.******@***.***>>
|
Beta Was this translation helpful? Give feedback.
0 replies
-
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment

Uh oh!
There was an error while loading. Please reload this page.
-
Hello,
I’m hoping you can tell me what I’m missing here. I’m trying to run some of the validation cases found on github for V7.7.5; currently looking at wall surface flux. Figure 10.1 indicates that the NIST/NRC Long wall and Short wall test CFAST runs are relatively accurate when compared to the test data. In fact, the Long Wall Heat Flux curve for NIST/NRC Test 8 shown on page 262 of the V&V Guide and reproduced in the attached file shows maximum flux values of about 3 kW/m2 and 4 kW/m2 for Targets 1 and 2 respectively.
However, when I run NIST_NRC_T8.in and plot incident flux curves for Target 1 and Target 2 from the devices.csv output file, I get different (lower) values; see attached.
The shape of the curves is about the same but the maximum flux values are lower at about 2 kW/m2 for Target 1 and slightly over 3 kW/m2 for Target 2. It seems the most likely reason I’m getting different results is that I’m not looking at the correct data. I want to look at wall surface flux and only the curves above from page 262 of the V&V Guide connect Target 1 and Target 2 flux to wall flux. There’s nothing in the input file itself other than that these targets are indeed located on the surface of the long wall. And there’s nothing I can find in the output files; that is, I can’t find a *.csv output file that has a column labeled “Wall Surface Flux.”
I note that the descriptive text provided in Section 10.1 (page 127) of the V&V Guide, for the NIST/NRC tests indicates that the actual measured flux values are net flux rather than gauge flux. But that would seem to show a need to alter the empirical test data in the curves presented above and on page 262, and I assume that has been done. It would not alter a comparison of the results I obtained using v 7.7.5 and those presented on page 262, also using v 7.7.5. Any light you can shed on this would be appreciated.
Thanks,
Ray
Wall Flux comparison of V&V Guide pg 262 to new case-1.pdf
Beta Was this translation helpful? Give feedback.